No, the outdoor tap rule for transformer secondaries (240.21(C)(4)) would allow the OCPD to be at the building supplied, outside or inside nearest the point of entry. The result is that the feeder consists only of the circuit conductors, with the grounded conductor as the fault clearing path.
Cheers, Wayne
You're calling the secondary supply conductors originating at the transformer a feeder.
I'm looking at 250.32 (B) (1) supplied by a feeder
250.32 (B) (1) exception # 2 does not give a description of a feeder without overcurrent protection at the supply side of the feeder.
250.32 (B) (1) exception # 2 gives a description of a feeder without an equipment ground
Looking at 250.32 (B) (2) supplied by separately derived system.
I see what you described addressed in 250.32 (B) (2) (b) without overcurrent protection provided where the conductors originate.
250.30 (A) do not rebond the grounded conductor on the supply side of the system bonding conductor.
If installed,
It is the supply side bonding jumper that connects the system bonding jumper to the buildings eguipment grounding and grounding electrode system.
Imo, 250.32 (B) (2) does not identify the secondary supply conductors as a feeder and does not give permission for a system bonding conductor at the building required disconnect