Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
This is pretty much what I said from what i could remember without looking up the code word for wordWith an outdoor transformer I think it is important to address the exceptions:
250.30(A)(1) System Bonding Jumper
Exception No. 2: If a building or structure is supplied by a feeder from an outdoor separately derived system, a system bonding jumper at both the source and the first disconnecting means shall be permitted if doing so does not establish a parallel path for the grounded conductor. If a grounded conductor is used in this manner, it shall not be smaller than the size specified for the system bonding jumper but shall not be required to be larger than the ungrounded conductor(s). For the purposes of this exception, connection through the earth shall not be considered as providing a parallel path.
and if you take advantage of that exception
250.30(A)(2) Supply Side Bonding Jumper
Exception: A supply-side bonding jumper shall not be required between enclosures for installations made in compliance with 250.30(A)(1), Exception No. 2.