What is meant by "stabilize the voltage to earth during normal operation" in 250.4(A)(1)?
buck33k said:What is meant by "stabilize the voltage to earth during normal operation" in 250.4(A)(1)?
I have never understood why the equipment would care what the voltage to earth would be. The equipment only sees the voltage between the circuit conductors. It doesn't care what the voltage to "earth" is.That's not considered a good thing.
How does a connection to earth prevent this? The spikes are are still there, the current is just shunted to ground. The grounding does not change the peek voltage of the transients.Where 'stabilizing voltage relative to ground' becomes important is that there are quite a few sources of high voltage, sources that could momentarily push the electrical system to damaging voltages relative to ground. If you simply had an ungrounded electrical system, then any of these voltage sources could damage the insulation system; simply walking across the carpet could produce enough voltage to punch through common building wire insulation.
If there is very little current there is also little energy so how does this low energy event become a problem?But these sources that I listed (excluding lightning) are _high impedance_ sources, meaning that there might be lots of voltage, but there is no current to back it up.
winnie said:...I presume that theory is what you understood 30 years ago, and now your experience gives you pause. ...
winnie said:...If I understand you correctly, the only issue (from the list above) that you have found actually causes enough of a voltage excursion to damage insulation is something like a re-striking ground fault....
winnie said:... At the same time, small static discharges (from people) have also become less of an issue (these discharges get shunted directly through the nearest computer chip)...
winnie said:...Did you know that theoretically, there is no difference between theory and practise...
I think you pretty well got it.winnie said:I am curious as to your understanding of why the NEC prohibits line to neutral loads in ungrounded and impedance grounded systems....
If I'm understanding, that would take a 4 buss panel so you could put in CBs on the neutral. Never thought of that - interesting idea.winnie said:...because in a ground fault the 'neutral' will be at a considerably elevated voltage. ... why not [add] a requirement that all conductors be treated as ungrounded. ...
I like it - good engineering.winnie said:...using small isolated impedance grounded systems for our motor test stands. This is not for continuity of service, but instead to reduce fault current. We measure ground fault current and open the supply contactor if it exceeds what we expect for capacitive loading. ...
Yeah, me too.winnie said:... I rather like the idea that the step between a ground fault forming and the supply opening is something other than a shower of sparks ...
No, it doesn't.winnie said:...This sort of use, impedance grounding with ground fault circuit interruption, does not seem to be anticipated by current code. ...
It is fine as long as it is supplied from a grounded wye system.Now, why don't they like 480V HID lighting?