stabilty test

Status
Not open for further replies.

vinod

Senior Member
Location
Saudi Arabia
Friends

What is the meaning of stability test for transformer or switchgear?
How can we perform this test?
What is the benefit of this test?
Please give some explanations...
 
test

test

I'm just glad it wasn't a stability test for inspectors...
 
What is the context? And who is asking for it? Unless this is a civil issue (earthquake?) I'm not familiar with it.

carl
 
stability of motor / transformer

stability of motor / transformer

Stability is conducted to check ct connection, relay settings to ensure during through fault / out of zone fault diffrential relay should not sense current and trip the breaker.
this is done by shorting LV side of trafo and appling reduced voltage by calculating fault current depend on trafo %impedence and confirms relay is not getting diffrential current in through fault, so ct connection relay setting ( in case numerical relays) is confirmed
 