We need to provide a 120v circuit to a chemical dispense unit that is a type Z purged/pressurized enclosure (I believe it's type Z, but am waiting for official response from vendor/installer). The enclosure is stainless steel and just has knockouts for power and communications termination and not threaded hubs. The room the dispense unit is located is rated C1D2. Being that this is a C1D2 environment and the enclosure is Z purged, per 501.15(B)(2)Exc.3: "Conduit systems passing from an enclosure or room that is unclassified as a result of pressurization into a Class I, Division 2 location shall not require a seal at the boundary.", do we not need to provide a seal within 18" of the enclosure? If not, would that change if it were a X or Y type pressurizing?
Since there is not a threaded hub on the pressurized enclosure, is there a specific fitting needed? Would we just installing a sealing locknut or hub suffice and is this covered in the NEC?
Thanks for the input