i recently submitted drawings to coral springs Florida to install a 30kw stand-by generator in a residential application with a 200 amp automatic transfer switch.
it was rejected by plan review stating that the generator kW rating was not enough to handle the existing load of 178 amps that was taken from the original load calculations that the city had on record.
we all know that load diversity is such that it is very unlikely that a generator with an output of 125 amps would ever be overloaded in a residential application as this. the generator has a built-in 125 amp main breaker that would trip if this event ever happened.
my understanding is that code article 702.5 takes this into consideration and allows us to size a generator based upon what loads will be operated at one time and allows the user to select the loads connected to the system and do load shedding if necessary. please comment!!
it was rejected by plan review stating that the generator kW rating was not enough to handle the existing load of 178 amps that was taken from the original load calculations that the city had on record.
we all know that load diversity is such that it is very unlikely that a generator with an output of 125 amps would ever be overloaded in a residential application as this. the generator has a built-in 125 amp main breaker that would trip if this event ever happened.
my understanding is that code article 702.5 takes this into consideration and allows us to size a generator based upon what loads will be operated at one time and allows the user to select the loads connected to the system and do load shedding if necessary. please comment!!