Re: stand-by generator sizing as per 702.5
Dave, the HVAC system does have a 10kw heatstrip which if turned on would increase my load by about 16 amps more than the a/c compressors RLA of 25. which would put the total load with every thing on at about 134 amps,but again every load would have to be on at the same time. Here in sunny South Florida we rarely ever turn on the heat, maybe once or twice the whole winter months, maybe never!!!
I know the code states to use the greater of the noncoincident loads, but i'm not sizing a service or feeder, i'm sizing a optional stand-by system according to 702.5.
We almost never have power outages in the winter months, it is always during hurricane season when it is very hot and the a/c units run continually. I agree with (iwire) the code is very clear on this issue, if the code required us to size a optional stand-by generator to the load calcs then 702.5 would not exist, It is the modifier to 220.40 that 702.3 speaks of.