Standard houshold 20 ampere AC receptacle to feed 12Vdc 200 ampere battery jumper /charger but how?

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Many years ago when I was a mobile mechanic working in automotive electrical systems, I wandered how I could make lighting on a house dim when jumping a 2000 Ford f450 7.4l turbo diesel with my 12 volt dc 200 ampere jump box for the trucks dc starter motor but yet not trip the household breaker for the receptacle circuit rated for only 20 amperes AC?

Hypothetically, what in the conversion process from AC to DC allows this to work?

If comparing power in both circuits (ignoring power factor, impedance, reactive qualities) you have

AC

120 volts x 20 amperes = 2400 VA on AC side of circuit

And

DC

12 volts x 200 amperes = 2400 VA on dc side


Although power whether in VA apparent or watts with power factor, I understand power is consistent in both but are not the AC household breakers rated to trip from excessive amperes current rather than power VA and WATTS?


I also understand that breakers have an inverse trip setting which would make me think the dc jumper would cause the breaker to trip thermally

I guess the equal power is the reason but I thought this was an interesting subject
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
It is kind of the same thing since the voltage applied to the circuit is known and mostly fixed, e.g. 120, 208, 240, ...

So a 120v 20A breaker is good for 2400 watts. A 20A breaker doesn't trip at 20.1 amps, it will hold much longer but diminishing as the current goes up. It would probably hold 25 amps for 10 minutes. Jumping a car is pretty quick, maybe 5 to 10 seconds. You could probably pull 30A or more out of a 20A breaker for that short period.
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
I was thinking that this concept may prove that ac home breakers are not so much about amperes but about watts power or VA

With voltage varrying current limitation can be any number
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Many years ago when I was a mobile mechanic working in automotive electrical systems, I wandered how I could make lighting on a house dim when jumping a 2000 Ford f450 7.4l turbo diesel with my 12 volt dc 200 ampere jump box for the trucks dc starter motor but yet not trip the household breaker for the receptacle circuit rated for only 20 amperes AC?

Hypothetically, what in the conversion process from AC to DC allows this to work?

If comparing power in both circuits (ignoring power factor, impedance, reactive qualities) you have

AC

120 volts x 20 amperes = 2400 VA on AC side of circuit

And

DC

12 volts x 200 amperes = 2400 VA on dc side


Although power whether in VA apparent or watts with power factor, I understand power is consistent in both but are not the AC household breakers rated to trip from excessive amperes current rather than power VA and WATTS?


I also understand that breakers have an inverse trip setting which would make me think the dc jumper would cause the breaker to trip thermally

I guess the equal power is the reason but I thought this was an interesting subject
If the primary side is 240 volts, what's the issue?
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
If the primary side is 240 volts, what's the issue?
The subject or issue is pulling 200 amperes for a few seconds from a 20 ampere breaker or even 100 or 50 amperes for an extended period of time without tripping a normal 20 ampere AC household receptacle circuit breaker
 