Keri_WW said:Do the major electrical companies (Square D, Eaton, etc.) all have a standard kAIC rating for the breakers?
Jraef said:You cannot assume anything any longer.
Ranch said:UL was mentioned, but it is so important to understand interrupt ratings as they pertain to both UL and NEC.
For US installations, google this -
Understanding The impact of NEC Article 409 & UL 508A
jim dungar said:These are two independent issues.
Ranch said:A good designer runs calculations to determine not only suitable SCCR ratings of circuit components but also the minimum AIC ratings of those protective devices that need to interrupt available short circuit current.
Independent categories (not issues) and they are side by side in the NEC. I prefer to look at SCCR and AIC at the same time. We are not fire fighters, we are fire preventer's no?
jim dungar said:NEC 409 and UL508A are two very limiting references (they only cover labeling of the SCCR of industrial control panels). The proper reference is NEC 110.10 which applies to all installed equipment including two of the most (in my experience) misused: automatic transfer switches and non-fused disconnect switches.
When you calculate the AIC requirements for a protective device are you making adjustments based on the X/R ratio of circuit?