In reading posts, I have seen a variety of ways in which voltages are being stated. Many seem to have a good handle on this topic, and therefore this post may not apply, however, I think it is of worthy mention to reaffirm how important it is, that as professionals, we do not become complacent in properly stating voltages.
ANSI provides a list of standard nominal system voltages, and voltage ranges, which are reprinted in IEEE Std 242. Also provided are the preferred voltages in bold type. For those who do not have access to these documents, I will provide the basics, for systems up to 480V. The information presented also applies for voltages above 480V.
The difference between 3 ph/3W and 3ph/4W is as follows:
3ph/3W are systems in which only the three current carrying conductors are brought out from the source to serve loads. A 3ph/4W system is one in which the three current carrying conductors and the grounded neutral are brought out from the source to serve loads. Stating the voltages for a 3ph, 3W system you only provide the line to line voltage. For 3ph/4W system you list the line to line voltage first then the line to neutral voltage.
Example: 208V and 480V (3ph, 3W), 480Y/277V and 208Y/120V (3ph, 4W)
Single phase systems are slightly simpler to define. You see them called out as 1ph, 3W, but in reality they are 2ph, 3W. A 1ph/2W system can also be used, but has no neutral brought out. No "Y" designation is used since the voltages are developed by other means than a wye connected transformer.
Example: 120/240V (1ph, 3W), 120V, 240V, and 480V (1ph, 2W)
For either single phase or three phase systems, indicating two different voltages, separated by a slash means a neutral is brought out of the source. If the system is derived from a "Y" system then it is also included. However, as will be demonstared this can be misapplied, and often times is.
Example: 240/120V, by definition is a 3ph, 4W system derived from a delta system, and should not be confused with 120/240V 1ph,3W system.
Other very common errors are the use of 120/208Y in place of 208Y/120V. Technically, 120/208Y is actually a 1ph, 3W system derived from an open wye configuration, whereas 208Y/120V is your common 3ph, 4W, wye system.
You also see 277/480V used in place of 480Y/277V.
Conclusion:
No matter what line of work you are in, when dealing with electrical systems it is very important that you understand the voltages you are working with, and that those voltages are conveyed properly on drawings, in calculations, and in written documents.
ANSI provides a list of standard nominal system voltages, and voltage ranges, which are reprinted in IEEE Std 242. Also provided are the preferred voltages in bold type. For those who do not have access to these documents, I will provide the basics, for systems up to 480V. The information presented also applies for voltages above 480V.
The difference between 3 ph/3W and 3ph/4W is as follows:
3ph/3W are systems in which only the three current carrying conductors are brought out from the source to serve loads. A 3ph/4W system is one in which the three current carrying conductors and the grounded neutral are brought out from the source to serve loads. Stating the voltages for a 3ph, 3W system you only provide the line to line voltage. For 3ph/4W system you list the line to line voltage first then the line to neutral voltage.
Example: 208V and 480V (3ph, 3W), 480Y/277V and 208Y/120V (3ph, 4W)
Single phase systems are slightly simpler to define. You see them called out as 1ph, 3W, but in reality they are 2ph, 3W. A 1ph/2W system can also be used, but has no neutral brought out. No "Y" designation is used since the voltages are developed by other means than a wye connected transformer.
Example: 120/240V (1ph, 3W), 120V, 240V, and 480V (1ph, 2W)
For either single phase or three phase systems, indicating two different voltages, separated by a slash means a neutral is brought out of the source. If the system is derived from a "Y" system then it is also included. However, as will be demonstared this can be misapplied, and often times is.
Example: 240/120V, by definition is a 3ph, 4W system derived from a delta system, and should not be confused with 120/240V 1ph,3W system.
Other very common errors are the use of 120/208Y in place of 208Y/120V. Technically, 120/208Y is actually a 1ph, 3W system derived from an open wye configuration, whereas 208Y/120V is your common 3ph, 4W, wye system.
You also see 277/480V used in place of 480Y/277V.
Conclusion:
No matter what line of work you are in, when dealing with electrical systems it is very important that you understand the voltages you are working with, and that those voltages are conveyed properly on drawings, in calculations, and in written documents.