I'm having trouble determining if the standby generator should be hooked up as a separately derived system or not and specifying the correct plug and receptacle. The application; mobile 100kw 3 phase 480/277 volt diesel generator set to supply one of three lift stations. These are located at different parts of the city. The concept is to move the genset to where it's most needed, quickly hook it up via plug and receptacles and manual transfer switch. The lift station is normally fed with 480v 3 phase power via overhead transformer bank, no neutral load, a dry type transformer 480/120 is used for 120 volt loads. My intention is to use a 4 pole plug/receptacle, 3 for the phase conductors, 1 for the ground. Is it still considered a "Separately Derived System" even though I'm not using the neutrals? Thanks.