tractormechanic
Member
I am installing a standby 20Kw LP generator using a 200amp (non load shedding) service entrance automatic transfer switch on a home with an existing 200amp panel. Our local inspector informed me that the generator needs to have the capacity to support everything in the 200amp service panel - referencing the 2008 NEC code changes. I would like to use a load calculation (article 220.87) to comply. Provided figures from the local electric company prove the highest month usage was 59KWH per day in a 30 day period last month. Can I use that figure to equate a 15 minute useage to be .6KWH and do you think this satisfies the requirement as stated in this code change?
Here is the change :
702.5 ? CAPACITY AND RATING
The sizing for Optional Standby Power Systems is now based on the type of transfer switch used; manual versus automatic.
(A) Available Short-Circuit Current. Optional standby system equipment shall be rated for the maximum available short-circuit current at its terminals.
(B) System Capacity. The calculated load on the standby source shall be in accordance with Art. 220 or by a method approved by the authority having jurisdiction.
(1) Manual Transfer Equipment. The optional standby power source shall have adequate capacity for all equipment intended to operate at one time. The user of the optional standby system selects the loads to be connected to the system.
Author's comment: When a manual transfer switch is used, the user of the optional standby system selects the loads to be connected to the system, which determines the system size.
(2) Automatic Transfer Equipment.
(a) Full Load. The optional standby power source shall have adequate capacity to supply the full load transferred.
Author's comment: If an automatic transfer switch is used in an optional system, the power source ? typically a generator ? must be capable of supplying the full load transferred. The load is determined by using Art. 220 as a basis on system sizing or an alternate method approved by the AHJ.
For existing facilities, the optional standby source can be sized to the maximum demand data available for one year or the average power demand of a 15-minute period over a minimum of 30 days [220.87].
This section was extensively revised and new subsections added in response to the growth of generator installations and the concern about the sizing of an optional standby source that uses automatic transfer switching.
If an automatic transfer switch is used in an optional system, the power source ? typically a generator ? must be capable of supplying the full load transferred. The load is determined by using Art. 220 as a basis on system sizing or an alternate method approved by the AHJ. However, the conditions are not the same for optional standby power supply when a manual transfer switch is used. In this case, the user of the optional standby system selects the loads to be connected to the system, which determines the system size.
Here is the change :
702.5 ? CAPACITY AND RATING
The sizing for Optional Standby Power Systems is now based on the type of transfer switch used; manual versus automatic.
(A) Available Short-Circuit Current. Optional standby system equipment shall be rated for the maximum available short-circuit current at its terminals.
(B) System Capacity. The calculated load on the standby source shall be in accordance with Art. 220 or by a method approved by the authority having jurisdiction.
(1) Manual Transfer Equipment. The optional standby power source shall have adequate capacity for all equipment intended to operate at one time. The user of the optional standby system selects the loads to be connected to the system.
Author's comment: When a manual transfer switch is used, the user of the optional standby system selects the loads to be connected to the system, which determines the system size.
(2) Automatic Transfer Equipment.
(a) Full Load. The optional standby power source shall have adequate capacity to supply the full load transferred.
Author's comment: If an automatic transfer switch is used in an optional system, the power source ? typically a generator ? must be capable of supplying the full load transferred. The load is determined by using Art. 220 as a basis on system sizing or an alternate method approved by the AHJ.
For existing facilities, the optional standby source can be sized to the maximum demand data available for one year or the average power demand of a 15-minute period over a minimum of 30 days [220.87].
This section was extensively revised and new subsections added in response to the growth of generator installations and the concern about the sizing of an optional standby source that uses automatic transfer switching.
If an automatic transfer switch is used in an optional system, the power source ? typically a generator ? must be capable of supplying the full load transferred. The load is determined by using Art. 220 as a basis on system sizing or an alternate method approved by the AHJ. However, the conditions are not the same for optional standby power supply when a manual transfer switch is used. In this case, the user of the optional standby system selects the loads to be connected to the system, which determines the system size.