Standby generator wire sizing

Hfalz1

Member
Location
Houston, Tx.
Occupation
Electrician
I am hooking up 22kW to 26kW standby generators and I am being told that a whole wire generac cable is good for 24kW and below. The cable contains 3-#3 cu and 1-#8 cu conductor. Also it has 6- #18 cu wires for the controls. The generator has a 100A breaker and the ATS is 200A. Is this correct? It seems to me the wire would have to be larger for the feeds.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
#3 is good for 100amps. Please update your profile to include your trade.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
So have you figured out how to fix your profile?
 
This thread talks about it in detail.

 
"Whole home" is a sales point of emphasis. In reality we size them according to load calculations. The ATS has a 100 amp breaker and usually load shedding ability built in to protect the generator and wire.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
it just brings me to put a picture.
Click on your name on the upper right, then click on account details.

Fill in the info you want in the various spaces, then click on save.

You can always make changes if you don't like how it appears.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If Larry's instructions don't work I can do it for you.
Let me know what it should be
 

MattG0311

Senior Member
Location
Illinois
Occupation
Apprentice Wireman
For 100a generator feeders, I like using #2 al SER.
Are you using 310.12 to size this feeder as it supplies the entirety of the home?

I ask because table 310.16 gives #2 AL an ampacity of 90amps.

I never thought of using 310.12 in a generator scenario and am curious if this is compliant.
 