Standby generator wire sizing

Birken Vogt

Senior Member
Location
Grass Valley, Ca
Are you using 310.12 to size this feeder as it supplies the entirety of the home?

I ask because table 310.16 gives #2 AL an ampacity of 90amps.

I never thought of using 310.12 in a generator scenario and am curious if this is compliant.

No reason it should not be compliant. But most jobs we do have load shedding and are actually fed with a 200 amp utility service. With load shedding I feel the conductors could be running close to their rating for longer and therefore 310.12 would not really apply.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Feeder conductors are never required to be larger than the service conductors.

I imagine the same rule applies even when there are no service conductors.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I think you can use 310.12 if you're backing up the whole home with the same size feeder as the service. Otherwise I don't think you can.
 