Are you using 310.12 to size this feeder as it supplies the entirety of the home?
I ask because table 310.16 gives #2 AL an ampacity of 90amps.
I never thought of using 310.12 in a generator scenario and am curious if this is compliant.
No reason it should not be compliant. But most jobs we do have load shedding and are actually fed with a 200 amp utility service. With load shedding I feel the conductors could be running close to their rating for longer and therefore 310.12 would not really apply.