Standby Generator
tomgilmartin
Vermont
I have an application for a standby generator which I would like to use to feed 2 separate buildings. The question is, does the Service Entrance code 230.3 apply to this generator? Specifically, can I run the output of the generator through building 1 to feed building 2?
Re: Standby Generator
Suggest you review the definition of "service" to start; it isn't a service. If possible, avoid this, especially if the buildings have separate services and 480V with GFI. If required, suggest 4 pole transfer switches. This isn't for someone not familiar with all the issues.
The current plan is for the buildings to have separate services. Building 1 has 3 25kva transformers on a pole, building 2 has 3 150kva transformers on a separate pole. Both are fed from the same 4160 overhead line.
If the buildings have different addresses, and could be sold separately, check the legal issues. We need to have easements and agreements written into the deeds.
Tom
What are you going to do when building 1 is still energized and you loose building 2, transfer building 1 so you can pick up building 2? You will still need a transfer switch at 2 to seperate from the utility. Why not install 2 transfer switches and two circuits from the generator and operate seperately?
[ October 03, 2003, 03:31 PM: Message edited by: bob ]
Originally posted by bob:
Tom
Bob,
Separate ATSs and circuits were my intention from the start, the question was whether I can run the feed for building 2 THROUGH building 1 (there is existing cabling), or whether I need to run the conduit from the generator OUTSIDE building 1 and then to building 2. Maybe that wasn't clear in the original post.
The NEC handbook, article 250.20 starts to answer you question. When a 4 pole transfer switch is used, the generator is listed as a "separately derived system." The definitions in 100 say a service is the serving utility, not a generator. Article 225.30 lists generator feeders. Article 225.37, for identification, mentions feeders passing through a building. This probably goes back to service conductors being protected by the Utility and not NEC requirements.