In a star start delta run application is there any advantage or disadvantage to having all 6 conductors in the same raceway?
Thanks
Thanks
What I was wondering, is do they all carry current at the same time?The delta connection is made at the motor starter so all 6 conductors make up to different terminals in the motor J-box, therefore all 6 carry current.
One thing that I never liked about the Y start Delta run several times I have seen where in older installs the timer failed and the motor burnt out because it stayed on the Y connection. Worst case a fellow sparky replaced a critical motor and only checked direction then walked away. A few minutes later they restarted the production line and replacement motor burnt up due to only running on the Y connection. We were taught to Megger every motor after replacing along with checking ampere on every phase at least twice after start up. Getting back to fire pumps we had the control panel with built in ATS transfer switch replaced on a 100 HP fire pump. They used the cheapest Joslyn Clark garbage contactors. On our 3 month fire pump PM'S we had to remove covers on the contactors. Cheap Joslyn Clark covers could not be removed to check contacts. We always did voltage drop measurements on contacts while motor was running along with IR scans.VFDs win hands down on centrifugal pumps and fans where flow control is part of the application or speed control improves a task. But if there is no value in varying the speed, they actually waste energy and cost too much. I personally prefer soft starters in that case vs Y-D for a number of reasons. Yet sone people stick to the old ways because they are either cheap (Y-D is still the least expensive form of Reduced Voltage starting, if only by a few percent), or they are technophobes. For sone reason the large refrigeration compressor industry is hanging on to Y-D in many areas, as are sone elevator mfrs.
Fire pump controllers need separate and expensive UL and FM listings, which are very difficult to achieve for any solid state controller like a VFD or Soft Starter. With a relatively short product design lifespan on electronics, the low sales volume on fire pump controllers makes it difficult to make the investment in testing, only to have to possibly start all over in 5 or 10 years when the components are obsolete. So you will still see Y-D there for sone time to come.
Just for discussion purposes, since Wye-Delta starting requires, as the name implies, a switching of the motor windings from one connection (wye) to another (delta). Switching the motor from wye to delta by the open transition method allows it to be completely disconnected from the power source for a brief time period before being reconnected delta.Just don't forget that you have six current carrying conductors and an ampacity adjustment of 0.8 is required.
Correct me if I'm wrong but I don't believe that this is true. When on Delta run all six conductors are carrying current at 58% of the motor rating. That's why those conductors are sized at 72% (58*125%=72%) of the FLC.So technically there are 6 CCC in the conduit and invokes Table 310.15(C)(1) Adjustment Factors for More Than Three Current-Carrying Conductors, the 6 conductors are never carrying current at the same time, only 3 at a time.
…the 6 conductors are never carrying current at the same time, only 3 at a time.
Yes, 40 hp but we Brits don't use hp, haven't for about 50 yars.These are Kai Feng Electric motors.
No hp on data plate.
30 kW so guessing 40hp???
Every one I have worked on had all six conductors carrying current in both the wye and delta connections. In the wye one set of conductors is connected to the 3 lines and the other set is connected together by the shorting contactor to create the wye. When you switch to delta the 3 conductors that were shorted in wye are connected to the 3 lines.Just for discussion purposes, since Wye-Delta starting requires, as the name implies, a switching of the motor windings from one connection (wye) to another (delta). Switching the motor from wye to delta by the open transition method allows it to be completely disconnected from the power source for a brief time period before being reconnected delta.
So technically there are 6 CCC in the conduit and invokes Table 310.15(C)(1) Adjustment Factors for More Than Three Current-Carrying Conductors, the 6 conductors are never carrying current at the same time, only 3 at a time.
Maybe a work around, not requiring the table ?
In reality, I've not used a Y-D starter in many years, since VFD's are relatively cheap, but it was something that crossed my mind.
Every one I have worked on had all six conductors carrying current in both the wye and delta connections. In the wye one set of conductors is connected to the 3 lines and the other set is connected together by the shorting contactor to create the wye. When you switch to delta the 3 conductors that were shorted in wye are connected to the 3 lines.