Is there any truth to the fact that operating these coils at 90% of rated voltage will burn up or damage the coil?
No there is no truth in the idea that operating a coil at a reduced voltage will cause it to overheat.
If the coil is run at a reduced voltage, it will draw less current and not more, and will run cooler not hotter.
This is not simply my opinion, but an observed fact which may be confirmed by measurement.
An electric motor worked at reduced voltage is liable to draw more current and may overheat, but that is because it is turning at almost the same speed, and therefore supplying almost the same HP as at full voltage.
However a contactor coil is not the same.
In years gone by, large contactor coils in the UK and perhaps elswhere, were fitted with an "economy circuit".
This consisted of a small auxilary contact, that once the main contacts had pulled in, inserted an impedance in series with the coil.
This reduced the voltage on the coil, to save power and reduce the heat produced. (the impedance was, on AC supplies, a small choke which looked like a flourescent lamp choke, and probably was)