090502-0820 EST
Larry:
A slight correction to your AC DC comment. If a relay is designed as an AC relay, then it has a shading coil, a slug of copper around a portion of the core to produce a phase shifted magnetic field in addition to the primary field. A relay of this type can be operated on either AC or DC but at different voltage levels. As an example KA5AY 120 V 60 Hz will pull in at about 37 V DC excitation. This relay did not show a large change in inductance relative to armature position. See the big difference in the A B contactor below.
A DC relay, no shading coil, can not be operated on AC because of the 120 Hz variation in magnetic force from 0 to maximum. Terrible noise. A bridge rectifier can be added to a DC relay to make it an AC relay, but now has lost the advantage of the AC relay in terms of pull in force.
broadgage:
No there is no truth in the idea that operating a coil at a reduced voltage will cause it to overheat.
If the coil is run at a reduced voltage, it will draw less current and not more, and will run cooler not hotter.
This is not simply my opinion, but an observed fact which may be confirmed by measurement.]
This statement is wrong for an AC relay using a shading coil, and of the structure of an AB motor starter. If your voltage is below the pull-in voltage, and the relay is not already pulled in, then because of the lower inductance of the magnetic circuit there may be a higher current thru the coil than at full voltage and the relay pulled in.
Here is some data on a 50 year old AB #2 709COD:
Dc resistance 41 ohms.
Following are 60 Hz measurements:
Voltage Current
..Volts......Amps
50 ........... 0.68
60 ........... 0.10 just pulled in
90 ........... 0.16
120 ........... 0.24
Note at 50 V the power dissipation in the coil is about 8 times that at 120 V. It will almost certainly burn out.
The coil inductance is 100 MH when the coil is de-energized, and 580 MH when I fully advance the solenoid plunger. These inductance measurements are at low voltage and 1 kHz. The corresponding calculated coil reactances are 37.7 and 218. If I calculate impedances from these values and the 41 ohms DC resistance and then use those values to calculate current I get higher current values than the measured values. May be a result of the 1 kHz measurement and the effect of the shading coil.