N Nurah New member Jun 4, 2009 #1 is there any code where recomend allowable percentage voltage drop for sizing the motor conductor for different controller or starter when starting? for example : DOL allow 20% VD at 6 x Full load current. What is allow for Reduce Voltage (soft starter) and VSD ?
is there any code where recomend allowable percentage voltage drop for sizing the motor conductor for different controller or starter when starting? for example : DOL allow 20% VD at 6 x Full load current. What is allow for Reduce Voltage (soft starter) and VSD ?
iwire Moderator Staff member Location Massachusetts Jun 4, 2009 #2 Code wise only fire pumps have voltage drop limits during start up, they are limited to 15% voltage drop at locked rotor current. Good design wise I do not know the answer.
Code wise only fire pumps have voltage drop limits during start up, they are limited to 15% voltage drop at locked rotor current. Good design wise I do not know the answer.
F farmaped Member Location PA - USA Occupation Engineer Jun 4, 2009 #3 That is good design (15% max). More than that will create much trouble will other equipment falling off-line, and your neighbors may notice. Should not be an issue with VSDs, just adjust your start accordingly.
That is good design (15% max). More than that will create much trouble will other equipment falling off-line, and your neighbors may notice. Should not be an issue with VSDs, just adjust your start accordingly.