Please evaluate a statement that an EE sent me.
Situation:
The Owner/GC sent me a Tenant Specification sheet and asked me to make sure we are providing the correct Electrical Service per this specification.
Tenant Requirements: " 1- 400 amp, 120/208v, 3 phase, 4w, panel w/ 400a 3 pole main breaker & 200a sub feed breaker and 1 - 225a MLO 120/208v 3P, 4W panel"
My Reply: "the requirements are not being meet. We have a 200a 277/480v 3P breaker feeding a 75kva transformer (with a max. amp of 208.2) feeding a 200a MLO panel"
EE Reply: "A 200 amp panel on 480/ 277 is equivalent to a 400 amp panel at 120/ 208."
Does this make sense to anyone?
Am I wrong?
Thank you.