nmui said:I'm trying to find out more information on the grounding requirements and testing of the ground for above-ground fiberglass duct. Any help?
Does it work? I would expect that it only works for a very small area around the conductive part. However it does not take much of a conductive path to prevent the build of of static....the IEEE Green Book says 1,000,000 ohms will do the job, so if the product in question has less than 1,000,000 ohms between the bonded points, there will be no static build up. I would expect the resistance of the plastic slides and the fiberglass pipe to far exceed a 1,000,000 ohms and there will be static build up with product or in the case of the slide people movement.Plastic sliding-boards and -tubes in kids' playground toys are often grounded at the rivets to reduce static potential.