If you know the steel is grounded.
		
		
	 
That is a good point. I know that the steel of all the buildings I 
service are bonded. It is a habit of mine to check the bonding jumpers
cold water,building steel, ufer, etc. everytime I enter a main electrical 
room,yes I'm a geek .
 This leads me to a question. If  Table 110.26 (A) (1) Condition 2 says that
"Concrete,brick,or tile walls shall be considered as grounded."
Why wouldn't a steel structure attached to concrete in multiple
locations be automatically be "Considered grounded" without a 
bonding jumper?  This is purely a hypothetical question.
Concrete walls are typically part of a concrete foundation.
Steel structural beams are typically attached to the footings
of a concrete foundation.