I have not seen an arrangement like this in some time and am scratching my head a bit. Please see image below- My plans show a "service breaker" in it's own enclosure (circled blue) between the utility meter socket and a non-service entrance rated ATS. The pad mounted generator is shown to be grounded as a non separately derived system as the ATS does not switch the neutral.
Also, a portable generator receptacle is to be installed on side of the outdoor control panel (plans showed 3W but it's 4W with neutral). This feeder connects in parallel with the Main/ATS feeder within the control panel on interlocked breakers.
Can anyone help identify if the main bonding jumper is shown in the correct location (in the control panel only), or if there are any code issues here I should take note of (particularly grounding & bonding) before I get too far into this one?