I am installing a new steam generator in a new location. The spec sheet states:
Input Voltage.....208-240VAC Single Phase
Kilowatt Rating....15.0
Maximum Amperage.......69 AMPS
I am using 240V. The paperwork also says use #4 wire and a 90amp breaker. So will this setup work?
A 90Amp breaker at main panel.
Approx 100feet of 1" EMT / flex.
(2) #4, (1) #8 ground.
A 100Amp? Non fused disconnect in the attic next to the steamer.
Input Voltage.....208-240VAC Single Phase
Kilowatt Rating....15.0
Maximum Amperage.......69 AMPS