DARUSA,
What are those 7 or 8 green conductors ( top left in your photo ) , what are they for ?
The bars are next to the switch gear these are the feeders ground wire.
I would think this is a violation of 110.54(B)?
That article is in refer to Tunnel Installations over 600 volt Nominal!!!
I don't see how it apply here.All conductor are installed in the same raceway with the feeder conductors, just terminated here on the bar.
The section require it is 300.3 B.
Ok but my water ground is going to be connected to the neutral at the service , my ground rod and the steel column will be attached to my grounding bar.just to tie all in the same point!!!! + the main bonding jumper!!!