No, the LOP is set to alarm and email through SCADA, as mentioned.
If we set it to open with LOP, then the breaker opens when the transmission line blinks, or a fuse blows between the CCVT and the relays for some reason. We don’t want that.
Also don’t want it closing with a voltage return...
if I get an alarm, I need to see why. Is a fuse blown? Is the CCVT out? Blade open?
I need to keep up with the alarm from our one remote station that charges batteries from the CCVT. Don’t want the batteries to run down.
On a a side note, if your using LOP on your project, are you also using UF? If so you may want to put a low voltage trip block on the UF logic.
Also undervoltage. If your using it you want to differentiate between UF, UV, and complete LOP with blocking logic.