kwired
Electron manager
- NE Nebraska
- EC
I'm just being overly cautious I guess. And possibly I still don't understand.
This is my (incorrect?) thinking:
On the secondary side of each transformer, there's X1 and X4. You have to pick one as the neutral and ground it or you don't establish 120 VAC across X1 to X4.
However I don't think you have to do that on the H1 and H4 600 V side since you're not pulling a Load at that point. I drew Neutral to Ground bonding in Red because I don't think its needed.
How far out in left field am I?
Any transformer secondary has voltage between secondary leads. If you don't ground any of them you have an ungrounded system, which is permitted by code with some requirements to go with it, but grounding the secondary is usually preferred.
Any conductor can be grounded, from a physics perspective. NEC generally will want you to ground a point that gives you lower volts to ground when possible - that is why "neutral" conductors are usually grounded.
A two wire secondary (disregarding x2 and x3 if they are not brought out as a usable circuit conuctor) has no "neutral" and therefore it doesn't matter which one you ground, either way results in same voltage to ground from the ungrounded conductor.