We have a 240v 1phase load that is about 1200 ft from the 240v panel. We want to use a 1 phase 240 to 480 transformer at the panel go 2 wire with egc through non metallic conduit and handholes to a 480 to 240 transformer with disconnect all mounted on a common metallic structure with the load.
It seems to me that to make these grounded systems I would have to ground 1 leg of 480 at the up transformer and 1 leg of 240 at the down. If I did that with a gec and bond at each transformer then my egc would create multiple ground paths.
I would prefer to go ungrounded between transformers but don't think it would be legal.
Any suggestions appreciated