Hi,
Long-time lurker, first-time poster here with a configuration I would like to get the hive opinion on.
I'm designing a 480kW, 480/277V PV system w/ 60kW Solectria string inverters. Although it's interconnecting into a 480/277V switchgear, the interconnect is located approximately 2,000' away from the array. I wanted to avoid stepping the voltage up, but it's just not practical to run 480V for this distance. I'm planning to step up to either 4,160V or 12,470V (most likely 4,160 but it will be a simple economic analysis) to transmit the power to the interconnection before stepping back down to 480V.
My proposed configuration is to step from 480/277V G-Wye to 4.16/2.4kV G-Wye at the array, then from 4.16/2.4kV G-Wye to 480V delta at the interconnect. The 480V side of each transformer would be protected by a 3-pole breaker, the 4.16kV side of each transformer would be protected by built-in expulsion and current limiting fuses.
Here's the thought process/justification:
On the utility side, it is prudent to specify an un-grounded configuration to avoid excessive neutral currents in the event of voltage imbalances. A delta configuration allows zero-sequence current to circulate, preventing zero-sequence harmonics generated by the PV inverters from passing through and providing an effective ground for the 4.16kV neutral. The 4.16kV system would be G-wye to allow the fuses to operate in the event of a ground fault on the MV system.
The inverters require a 4-wire system, so this constrains the primary (inverter) side of the step-up transformer to a Wye-G config. Given that the utility is isolated at the step-down transformer and there won't be any voltage/current monitoring on the MV system, the G-Wye 4.16kV configuration would minimize any chances that a lost-phase on the MV system would go un-detected by the inverters. Although a Delta winding would work, I believe this introduces the possibility of the inverters continuing to produce power even if a phase is lost on the MV system due to the single phase fusing used for protection.
If there is a phase lost on the interconnection side than this may not be detected by the inverters due to the delta winding. Unlike the MV feeder, there will be a revenue meter on the interconnection side so the voltages can be monitored and addressed if there is an issue. Also the facility would notice this phase loss as well.
This appears to be a relatively straight-forward design but I like to get alternate opinions, any thoughts?
Long-time lurker, first-time poster here with a configuration I would like to get the hive opinion on.
I'm designing a 480kW, 480/277V PV system w/ 60kW Solectria string inverters. Although it's interconnecting into a 480/277V switchgear, the interconnect is located approximately 2,000' away from the array. I wanted to avoid stepping the voltage up, but it's just not practical to run 480V for this distance. I'm planning to step up to either 4,160V or 12,470V (most likely 4,160 but it will be a simple economic analysis) to transmit the power to the interconnection before stepping back down to 480V.
My proposed configuration is to step from 480/277V G-Wye to 4.16/2.4kV G-Wye at the array, then from 4.16/2.4kV G-Wye to 480V delta at the interconnect. The 480V side of each transformer would be protected by a 3-pole breaker, the 4.16kV side of each transformer would be protected by built-in expulsion and current limiting fuses.
Here's the thought process/justification:
On the utility side, it is prudent to specify an un-grounded configuration to avoid excessive neutral currents in the event of voltage imbalances. A delta configuration allows zero-sequence current to circulate, preventing zero-sequence harmonics generated by the PV inverters from passing through and providing an effective ground for the 4.16kV neutral. The 4.16kV system would be G-wye to allow the fuses to operate in the event of a ground fault on the MV system.
The inverters require a 4-wire system, so this constrains the primary (inverter) side of the step-up transformer to a Wye-G config. Given that the utility is isolated at the step-down transformer and there won't be any voltage/current monitoring on the MV system, the G-Wye 4.16kV configuration would minimize any chances that a lost-phase on the MV system would go un-detected by the inverters. Although a Delta winding would work, I believe this introduces the possibility of the inverters continuing to produce power even if a phase is lost on the MV system due to the single phase fusing used for protection.
If there is a phase lost on the interconnection side than this may not be detected by the inverters due to the delta winding. Unlike the MV feeder, there will be a revenue meter on the interconnection side so the voltages can be monitored and addressed if there is an issue. Also the facility would notice this phase loss as well.
This appears to be a relatively straight-forward design but I like to get alternate opinions, any thoughts?