Not required to be a grounded system unless the neutral is being used as a circuit conductor. If it is not a grounded system, ground detectors will be required.Is the secondary Wye connected?
If so you are required to have a SBJ to ground
Sorry I answered and didn’t post. I had a 480V motor controller, the control power secondary was not grounded. It was very difficult to TS the control wiring as there was no ground reference
Yes an ungrounded system can be more difficult to troubleshoot. One of our clients used ungrounded 120 volt control power for their motor controls. The first thing I would do when I had to troubleshoot that system, was to add a temporary grounding connection.