What he dod was tie the x0/h0 to gndSeems to me this has already been tried (without a primary feeder neutral) and...
not the source x0
I would never do this. I want the transformers primary windings to be able to accommodate imbalanced currents by letting the voltage 'move around'. Tying the X0 to a grounded reference point forces the voltage relationship to be fixed, in this case at 277V, which means the winding currents may need to increase beyond the load current.
No they wouldn't
any imbalance would flow in the neut
it's done all the time
but I would have gone
wye-delta-wye to begin with
not wye-wye-wye
That's what I said... just using different words. :slaphead:What he dod was tie the x0/h0 to gnd
not the source x0
They are only isolated if you remove the jumper shown on the nameplate.But in this case the h0/x0 are electrically isolated
not the same
And that was the suggestion I agreed withThey are only isolated if you remove the jumper shown on the nameplate.
Perhaps the breaker failed from severe overvoltage.....either from a floating neutral that went L-L or from resonance. If the local end has the neutral adequately grounded or if the breaker is, in fact, rated at L-L then, my money is on resonance.
...my money is on resonance.
OP mentions the system has been up and running with power fluctuations once or twice a month... which is a fairly good indication by my understanding (which is not very good btwNot enough detail for guesstimates about cause. Did the fault occur during commissioning?
Or it could have been the breaker itself. I recall a ground-fault occurring in the draw-out carriage of a breaker! Unfortunately, there was no “bus stab” for ground, so, the fault-current had to travel thru the wheels on the carriage! The result was loss of 20-30 ft of (approved) LV switchgear!
Phil
OP mentions the system has been up and running with power fluctuations once or twice a month... which is a fairly good indication by my understanding (which is not very good btw) of a resonance problem.
You're just looking at the failed breaker. The grounding was revised after that mishap.Xfmr certainly fits the "L" component of Resonance, but to date no evidence of the "C" component! OP said 15 ft between step-up xfmr and open HV disconnect. No word yet on"resonance" markers!![]()
Phil
The HV disconnect has to have been closed for the system to be getting power fluctuations once or twice a month. :slaphead:
Any chance the resonance problem stems from the primary side of this transformer?