Commercial? Residential?

Are they service conductors or a feeder? Inside a building or outdoors? Etc Etc.

If you want a real answer you have to post ALL the details.
 
How do I parallel a 400 amp s. phase service to two 200 amp panels 250 feet away

Steve,

As you may gather from some of the responses we need more information to answer the question. And don't let some sarcasm dissuade you.

Welcome to the Forum. :)
 
Steve,

As you may gather from some of the responses we need more information to answer the question. And don't let some sarcasm dissuade you.

Welcome to the Forum. :)

Yeah, and we wonder why people post one time and after all the smartass replies they never post again......
 
How do I parallel a 400 amp s. phase service to two 200 amp panels 250 feet away
Steve,

Firstly, we will assume (I will anyway) that you are coming from a 400/320 Meter Enclosure to (2) separate 200A panels. This would not be a parallel application in its nature. But it does lead to other questions. Since you are new to the forum (I am new myself:roll:) make sure the questions that you ask have as much detail as possible because it makes a difference in the responses.

If your meter enclosure has double lugs then you can come out with a separate 4/0 AL and keep the calculated loads under the respective value given in 310.15(B)(16) or 3/0 CU if you choose.....and keep in mind any adjustments or corrections that may apply along the way.

Based on the brief description I would say ignore 310.15(B)(7)(1) as it does not seem to apply in your example. Can't also tell because you did not express if it was a 120/240V application or otherwise....again the devil is in the detail.

The more accurate the question the more accurate the responses....Welcome to the Forum !
 