I need to order a 800 amp switch gear it has a high leg. What voltage do they come in are they like disconnects 250,600 etc or do they come 120/208 and so on
You mentioned the term "switchgear". Is there a specific application that you have in mind, where switchgear specifically is needed? Or is this a catch-all term that also includes panelboards? The reason I bring this up, is that panelboards are much more common at the scale of 800A, than switchgear.
As others have mentioned, it is the breakers that would "care" about the difference between 120/208V wye systems,and 120/240V high leg systems, because of the slash rating that limits you to 120V to ground where applicable. The high leg exceeds 120V to ground, so slash rated breakers cannot touch that phase. The alternative is straight-rated breakers, where both the the line-to-ground and line-to-line voltage can be as high as the only voltage rating that is mentioned on the datasheet. It is common that 3-pole breakers are straight-rated, while 1-pole breakers are slash rated with few (if any) exceptions. 2-pole breakers are common in both rating types.
How expensive are 240V rated breakers compared to slash rated 120/240V versions? Have not needed one but have been told they are pricey, what brand, plug in, VS bolt on, will affect the price of course.
I wager most of of have done it. I'll confess I have.Slash rated breakers were installed for years on the high leg. Common enough in older installations. IDR when it started to be Red Tagged by our SED, but I do know it was allowed in the past.
According to this article:
http://ecmweb.com/content/understanding-circuit-breaker-markings
"Single-pole breakers are always slash rated."
"Two-pole breakers can be either slash or straight voltage-rated, whereas 3-pole breakers are all straight voltage-rated."
I believe that the GE TEY 3 pole breakers are also slash rated 480/277.Just a comment, I think that is true for 250V breakers, but not for 480V breakers. For example a Siemens BQD is only slash rated for 480/277.
My 1967 Square D literature shows both 120/240V and 240V 2 pole breakers, so I would assume slash rated breakers were actually never allowed on the 208V leg.Slash rated breakers were installed for years on the high leg. Common enough in older installations. IDR when it started to be Red Tagged by our SED, but I do know it was allowed in the past.