dvcraven0522!

Member
Location
St. Louis
Occupation
Electrical Design
I have attached a couple of screen shots showing a floor box with (2) receptacles. One of the receptacles feeds piece of equipment several feet away with a flexible cord passing through another piece of equipment. Seems high irregular to me.
 

Attachments

  • Screenshot 2023-12-15 154506.png
    Screenshot 2023-12-15 154506.png
    9.6 KB · Views: 20
  • Screenshot 2023-12-15 154612.png
    Screenshot 2023-12-15 154612.png
    11 KB · Views: 20
That looks like a flexible cord will be hidden behind drywall. Absolutely not permitted. Don't have my code book handy, but someone will likely add the citation.
 
Thanks Charlie I always respected your thoughts. The equipment is actually free standing on the floor in a Mobil on the run gas station.
 
How is the flex cord routed? Is it essentially a regular plug and cord connection with the cord running along the floor?
 