Minimum size circuit for a stove top, A 240 volt 6.4kw, 26.7 amps. would this be allowed to be fed with #10 romex on a 30 amp breaker in a dwelling? Direct wire.
More specifically "Note 4".ramdiesel3500 said:See 220.55.
ramdiesel3500 said:See 220.55.
RUWired said:wireman, If you cord and plug this cooktop, then you'll have to go with the 80% rating as in 210.23(B).That will mean upsizing to a 35a breaker and #8 awg if useing rx.If you hardwire then your ok with the 30a circuit. Table 220.55 is allowed for sizing branch circuits as per 210.21(B)4.In your case you need to read note 4 of table 220.55 for a single cooktop.(name plate rating).
Rick
The 2005 NEC doesn't mention receptacles in table 220.55 Note 4. It specifically states that it is permissible to calculate the branch circuit "LOAD" for a counter mounted cooking unit by the nameplate rating of the appliance. I don't have my 2002 with me right now.wireman3736 said:I read 210.21(B)(4) and this is talking about the range receptacle rating,
I don't know if this means the circuit rating, just trying to make sure.![]()
hillbilly said:The 2005 NEC doesn't mention receptacles in table 220.55 Note 4. It specifically states that it is permissible to calculate the branch circuit "LOAD" for a counter mounted cooking unit by the nameplate rating of the appliance. I don't have my 2002 with me right now.
steve
My computer is acting funny please for give this post, 210.23(b) only applies when more than one outleet or receptacle is supplied , this is an idividual branch circuit and can supply any load for which it is rated.RUWired said:wireman, If you cord and plug this cooktop, then you'll have to go with the 80% rating as in 210.23(B).That will mean upsizing to a 35a breaker and #8 awg if useing rx.If you hardwire then your ok with the 30a circuit. Table 220.55 is allowed for sizing branch circuits as per 210.21(B)4.In your case you need to read note 4 of table 220.55 for a single cooktop.(name plate rating).
Rick
M. D. said:My computer is acting funny please for give this post, 210.23(b) only applies when more than one outleet or receptacle is supplied , this is an idividual branch circuit and can supply any load for which it is rated.