Stranded #18 wire in conduit, re-purposed from low voltage to AC

Status
Not open for further replies.

brycenesbitt

Senior Member
Location
United States
I'm trying to solve a retrofit problem inexpensively. Would anything in the NEC prevent re-purposing #18 stranded wire in conduit for use with an 110V circuit, given a properly sized over-current device? This is two or four wires pulled through conduit, #18 copper stamped 300V, with runs of 150 feet or so. The wire was originally pulled for fire alarm sensors in 1977 and operated at 24 volts DC. Would any special requirements apply to the wire? How would you mark this to the 'next guy' is not confused/laugh too hard? Note that the proposed AC loads are well within the ampacity of the wire.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I'm trying to solve a retrofit problem inexpensively. Would anything in the NEC prevent re-purposing #18 stranded wire in conduit for use with an 110V circuit, given a properly sized over-current device?
Yes there is. Smallest conductor you can use is 14AWG. Don't have the section at my ffingertips, but there is someone here that does.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
if it fits in article 725 you can reuse them. there may be other sections that allow it as well, but for the most part you can't use #18 for normal NEC wiring.
 

brycenesbitt

Senior Member
Location
United States
The end attachment would be a series of 120V consumer smoke detectors. Clearly current draw is
not an issue with the #18 wire. I can yank out the #18 wire and pull #14, but it would be for no reason other than code compliance and reduction in confusion. Finding the appropriate breaker might also be a problem ;-).
 