I agree. Think of all of the existing pigtails and stranded conductors terminated on an EGC bus, neutral bus, or circuit breaker, there are tens of millions without issue.If that was a problem, all the millions of terminations using stranded wire would be in jeopardy!
Wire stranding — Unless clearly marked "Solid," "SOL," "Stranded" or "STR" for a given wire size, wire range or wire combination, conductors in the range 30-10 AWG are both solid and stranded, and 8 AWG and larger are for stranded wire only.
Where I've seen potential issues is with neutral bus of some older QO loadcenters. They often had a clip in certain spots (or all on some neutral bus segments) that I believe was necessary for them to be listed for use with stranded conductors and these clips seemed to end up missing often. Current design is no longer that way though.UL 67 requires that the wire termination points in a panelboard assembly comply with "UL-468A/468B, Wire Connectors". The UL Guide Information for "Wire Connectors and Soldering Lugs (ZMVV)" says:
Wire stranding — Unless clearly marked "Solid," "SOL," "Stranded" or "STR" for a given wire size, wire range or wire combination, conductors in the range 30-10 AWG are both solid and stranded, and 8 AWG and larger are for stranded wire only.UL 67 requires that the wire termination points in a panelboard assembly comply with "UL-468A/468B, Wire Connectors". The UL Guide Information for "Wire Connectors and Soldering Lugs (ZMVV)" says:
The only connection from the branch circuit neutral to the panel neutral bus is through the circuit breaker so all of the neutral current is flowing through that connection to the bus.Not that it OFFICIALLY makes a difference, but that neutral pigtail on a GFCI (or AFCI) is only there to provide 120V to power the tiny little printed circuit board inside. So the current draw is milliamps and if a few strands get cut, it’s not going to really affect anything.
I think Jraef had a brain cramp, he should know this. Single pole GFCI - what current goes out on ungrounded conductor will be coming back and passing through that white pigtail on it's way back to the source if you don't want it to trip on GFCI function.The only connection from the branch circuit neutral to the panel neutral bus is through the circuit breaker so all of the neutral current is flowing through that connection to the bus.
Wow, I've been putting my 6 solid GEC in the wrong holes for decades. I feel so ashamed.UL 67 requires that the wire termination points in a panelboard assembly comply with "UL-468A/468B, Wire Connectors". The UL Guide Information for "Wire Connectors and Soldering Lugs (ZMVV)" says:
It could be marked for both on the label.Wow, I've been putting my 6 solid GEC in the wrong holes for decades. I feel so ashamed.