Stranded wire .... Bare, soldered, Ferrule.....which?

Status
Not open for further replies.

klaatu

Member
Location
Texas
Occupation
Engineer
When dealing with stranded wire under a lug screw, what is best practice and what is permitted under NEC?
For example, simply use the stranded wire bare or add a ferrule to keep the strands together and less compressible, or solder the end to make it firm and bound and less compressible.

Several examples recently where the lug was torqued down, but many of the strands were not captured. Other instances where after torqueing and later removing, the wire was deformed and could not be reinserted, and had to be cut off. Which is okay, unless there no extra length.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
"Standard" stranding (Chapt 9 Table 8) or fine strand (Chapt. 9 Table 10) ?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
When dealing with stranded wire under a lug screw, what is best practice and what is permitted under NEC?
For example, simply use the stranded wire bare or add a ferrule to keep the strands together and less compressible, or solder the end to make it firm and bound and less compressible.

Several examples recently where the lug was torqued down, but many of the strands were not captured. Other instances where after torqueing and later removing, the wire was deformed and could not be reinserted, and had to be cut off. Which is okay, unless there no extra length.
Ferrules are not intended to be used on the type of screw terminals found on electrical receptacles. I would suggest a fork terminal instead.

I kind of agree that stranded wire is not ideal for terminating on these kind of screw terminals.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Ferrules are not intended to be used on the type of screw terminals found on electrical receptacles. I would suggest a fork terminal instead.

I kind of agree that stranded wire is not ideal for terminating on these kind of screw terminals.
From the UL Guide for Receptacles for Plugs and Attachment Plugs (RTRT)
Terminals of a receptacle are permitted for use with certified field-installed crimped-on wire connectors or an assembly, if so identified by the manufacturer.
There is only one model of receptacle from one brand that is so identified.
 

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
What is a lug screw? Is this a terminal or a binding screw on something like a receptacle?
I assume he means mechanical lug type.

They are typically wire size dependent. Sounds like it's pushing the limits on size or has the incorrect size even.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
When dealing with stranded wire under a lug screw, what is best practice and what is permitted under NEC?
Always used listed crimp tool matched to listed fork terminal, but also seen field stripping methods that keep all strands under the terminal.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It is still not clear (to me) if you are addressing small conductors (`14-10) and screw terminals or larger conductors and pressure terminals.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
It is still not clear (to me) if you are addressing small conductors (`14-10) and screw terminals or larger conductors and pressure terminals.
It appears Klaatu has left the building. If interested, others must resolve this question without further direction
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
This forum is awesome....I have thought since I was a kid it was "varada"...I am learning something new every day.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Yes, one of the Hubble lines is identified for use with fork terminals. No others that I know of.
Is that possibly listed for Aluminum fork terminals, which are typically sold everywhere, vs harder to find steal or copper terminals?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
This forum is awesome....I have thought since I was a kid it was "varada"...I am learning something new every day.
This is the exception and not the rule. Don deserves the credit for sharing this, not the forum.

Few can share details about listing requirements, much less provide referenced sources. Listings requirements are especially difficult to show, since standards are not free, and there's little incentive to put it in public domains, with often thankless trolls that cause more grief than reward.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is that possibly listed for Aluminum fork terminals, which are typically sold everywhere, vs harder to find steal or copper terminals?
No idea. Don't think I have ever seen aluminum fork terminals. The ones I use have always been tin plated copper.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
This is the exception and not the rule. Don deserves the credit for sharing this, not the forum.

Few can share details about listing requirements, much less provide referenced sources. Listings requirements are especially difficult to show, since standards are not free, and there's little incentive to put it in public domains, with often thankless trolls that cause more grief than reward.
Actually all of the UL Standards can be viewed using the same non-user friendly system that the NFPA uses for their free viewing. You just have to register with an e-mail address.
 