I have a 240V 3PH outlet that I am plugging in a 240V Delta to 480V Delta transformer. When I check the voltage to ground at the outlet, I get 240V between L1-G, L2-G, and L3-G. This all appears fine. But when I check the phase to phase voltage, I get 240V betwee L1-L3, 240V between L2 and L3, but less than 1 volt between L1 and L2.
My immediate instincts was that it could be a corner grounded delta system, but it doesn't add up. I still should be reading 240V between phases on a corner grounded delta system, right? Why would I be seeing 240V L-G, and 240V Ph-Ph except on L1 and L2 where I only see less than 1 V?