Strange 3-way Switch Problem
Little Bill
Tennessee NEC:2017
Semi-Retired Electrician
I saw this on another Forum. Thought it would be a good discussion here.
Problem was on a new house where one 3-way circuit wasn't working right.
Power in one box with 12-2
12-3 ran from 1st box to 2nd box, white as the neutral, red and black as travelers
12-2 from 2nd box to light, whites/neutral tied together all the way from box 1 to light
Light works, but switch at 1st box doesn't turn the light off
Switch at 2nd box turns the light on/off, like a single pole
Switches have been replaced and problem still exists
A piece of 12-2 was ran between boxes as a test, only replacing the travelers as the neutral is good because the light does work
With the jumper ran, both switches work like they should
Now, your thoughts as to what is wrong?
Call the ungrounded conductors at the two ends of the 12/3 R1, B1 at switch 1 and R2, B2 at switch 2. Presumably the 12/3 does not have the expected continuity of R1-R2 and B1-B2 with no other continuity, as replacing the travelers fixes the problem.
A failure of the form R1-B1-B2 all connected and R2 floating would explain the behavior. Or similarly R1-B1-R2 all connected, and B2 floating.
Cheers, Wayne
Cheers, Wayne
Right…in other words, one of the travelers is open, plus they are shorted together on the switch 1 side of the open conductor.
12/3 traveler is compromised? What does continuity check show on the travelers?
Replace the installer, especially if he doesn't have a meter to easily figure out what is wrong. Sorry this is so basic I have very little tolerance.
That's the theory. With flat XX-3 NM cable, the red is on one side, the white is in the center, and the black is on the other side. I'm trying to figure out how the cable could be damaged enough to sever one traveler, nick the other and short them, and not cause damage to the neutral and short it to the travelers.
The electrician that is troubleshooting it did not install the cable. His thinking is a screw, nail, or staple hit the cable. The HO did his own wiring.
He said the travelers had continuity. I can only guess that it maybe had enough continuity for the meter to read it, but not enough to carry current.
If the HO did his own wiring, that opens a whole can of worms. He could have a j box somewhere that he failed to mention, that he messed something up in.
As others have stated, the 2 tests are: pull the 3 way switch and check for proper functioning. I once wired a new house and out of the 12 3 ways I installed, 7 were non functional. They were Leviton. It was verifiable with a meter. Platt took them back. I was pissed to say the least.
Number two is ohm out the travelers.
Or 3, abandon the 12-3, pull a new one, hook it up and get paid. 👍
The guy said he changed the switches.
He is replacing the cable. He said final inspection was coming up so he wanted to get it working.
I agree. Got a meter?? Know how to use it?? Know how to test a 3 way switch?? Know how to extend you meter leads with some ramen?? It's very simple: measure resistance on each conductor, and resistance between each conductor. Unless there is flux capacitor or non transverse quantum voltage transducer in a buried j box, the physics won't lie.
Just thinking about this now. I wonder if the box were the switch was behaving like a single pole had one or more feeds and the traveler terminals were actually connected to a grounded and ungrounded conductor, and not the actual travelers from the first switch. With the switch in one position, there would be continuity between the ungrounded and common and the light would be on. With the switch in the other position, the common terminal would be connected to the grounded conductor and the light would not be on, since it would be connected to two grounded conductors.
According to the guy's statement, and pictures, this is what he has in each box.
Box 1: 12-2 coming in as the feed/hot
12-3 going to box 2
Box 2: 12-3 coming in from box 1
12-2 going to light
That's it.
I have seen where someone connected one of the wires to the green screw rather than the correct location. I don't recall if they were using a single pole switch in place of a failed three way, or just wired a 3 way wrong.
When I get something like that, I don't even get the meter out.
1) Connect hot to the black traveler in the first box. Connect black traveler to the black from the light in the second box. Light should light.
2) Connect hot to the red traveler in the first box. Connect red traveler to the black from the light in the second box. Light should light.
If the light lights in both tests the switches are wired wrong or bad. If one or the other test does not light the light check the traveler wiring.
-Hal
12-3 going to box 2
12-2 going to light
That's it.
Hmm, I see. Just seems very unlikely for a cable to go bad in the way it did. It seems like an event along the odds of winning the lottery.
Wonder if there are any additional cables in the light fixture box.
We will never know the damage/cause as the guy ran a new 12-3 between boxes to get the light going. The light and switches were in a stairwell and he thinks a screw for the handrail hit the cable. This would be a one in a million shot because of how the conductors are laid in the cable. Most XX-3 cable has a red on one side, neutral and EGC in the middle, and the other traveler on the other side. It's hard to understand how one traveler could be cut completely, the other traveler nicked, and both travelers shorted together. All this without damaging the neutral. You would think either the neutral or EGC would have shorted to a traveler and tripped the breaker.
If I was doing this, I would have insisted on removing some drywall so I could see this phenomenon. Or at least remove the screws and hand rail to see if the short cleared.