Strange Plug and Receptacle

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Can anyone tell me anything about this plug or the accompanying socket? It looks like it was semi popular at one point being use on equipment, in buildings as a standard receptacle and even listed in several old electrical books going as far into 70s. No in-depth description however.

Also interesting in that this combination is listed as being polarized but apparently there is a duplex version which swaps live and neutral. Equipment drawings also seem to display an indifference to polarity relative to each other. ie two competing standards as to which side is hot and which was supposed to be neutral.



 
They used to be pretty standard on large wall/window air conditioners. When used with 240v they often did't have an EGC. You can still buy them, McMaster has them in stock.

1603170639536.png
 
Why is there no 10-15P?
Same reason legacy NEMA 10–30 outlets for 3-wire 230v Electric dryers are replaced by NEMA 14-30 outlets. NEMA 10 series is missing the grounding prong when neutral is used for control circuits.
 
That obsolete configuration is what the current plug/receptacles used in Australia, & New Zealand are based on, the domestic ones used to be rated 20A 250V, they were changed to the current rating of 20A 125/250V.
 
Yes, I believe that used to be called a "crow foot" receptacle.

Yep, standard Crows Foot plug/receptacle. I'm surprised you have not seen them before. Very common on small 220 volt (yes, I said 220, since it is an old design :D ) single phase tools, like table saws, AC units, air compressors, pumps installed before the 80s.
 
Same reason legacy NEMA 10–30 outlets for 3-wire 230v Electric dryers are replaced by NEMA 14-30 outlets. NEMA 10 series is missing the grounding prong when neutral is used for control circuits.

Right, but you could ground through the neutral until 97. NEMA 10-15 dropped out the race before that.
 
yes, thank you for refreshing my memory, 3-wire outlets for dryers are only allowed to be grandfathered on older properties and appliances.
 
yes, thank you for refreshing my memory, 3-wire outlets for dryers are only allowed to be grandfathered on older properties and appliances.
I always recommend to all my customers that they upgrade to 4-wire when they have 3-wire electric dryers and/or ranges. I explain that the 4-wire design is much safer than the old 3-wire. Since many people are afraid of electricity, most will go ahead with the upgrade. The only time I don't mention it is when upgrading will be difficult (such as finished walls or in homes without basements).
 