Let me first apologize for this partially being an HVAC control question.
I am on call this weekend, and I get a no heat call from a commercial customer. He tells me that the feeder faulted, and toe POCO has him on a generator. This led me to think that a phase monitor in the rooftop tripped out due to incorrect rotation. No such luck. Found the control board which is fed from a 208 / 24 transformer throwing a "control fault" code (immediately after it powers up. Replaced said board, and the unit fires up, for about 45 seconds..... and i have inducer full flame etc. Unit goes out, and again throws me the same code as before.
Now here is the question, the generator is connected to the incoming service conductors ( they are still connected to the POCO transformer with the primary legs disconnected ( this is where the fault is). No one has changed any of the service grounding and bonding past the transformer (m rotation is correct too). Any ideas how merely adding the generator can create such an issue as I have? Usually the issue I have is caused by improper polarity or a bad ground. I appear to have none of these, just cant figure out how the gennie is causing me this much trouble......
Howard
I am on call this weekend, and I get a no heat call from a commercial customer. He tells me that the feeder faulted, and toe POCO has him on a generator. This led me to think that a phase monitor in the rooftop tripped out due to incorrect rotation. No such luck. Found the control board which is fed from a 208 / 24 transformer throwing a "control fault" code (immediately after it powers up. Replaced said board, and the unit fires up, for about 45 seconds..... and i have inducer full flame etc. Unit goes out, and again throws me the same code as before.
Now here is the question, the generator is connected to the incoming service conductors ( they are still connected to the POCO transformer with the primary legs disconnected ( this is where the fault is). No one has changed any of the service grounding and bonding past the transformer (m rotation is correct too). Any ideas how merely adding the generator can create such an issue as I have? Usually the issue I have is caused by improper polarity or a bad ground. I appear to have none of these, just cant figure out how the gennie is causing me this much trouble......
Howard