Nope ............................
I have never seen a listed romex staple or pipe strap.
I wouldn't immediately reach for a one hole to secure romex, but...
...I don't see where the straps or staples are required to be listed. So long as you can convince the inspector and/or AHJ that it's acceptable, then it's fine, 90.4.
I'd just drive a staple into the stud (without securing a cable with it), and secure the cables to the staple with a zip tie. Done.
Well...here is yet another example of using anything for any purpose - as long as it 'works'. What is the purpose of listing products, if this is acceptable? Why not use a piece of old nylon strapping across the romex and secure it with two drywall screws? Or better yet, use a protector plate bent over the romex and secure it with nails.
Ultimately, it all comes down to the AHJ and what they will "approve"....A listing makes it easy as long as the product that is listed is being used in the application for which it is listed. I don't understand why this is so hard for folks to understand?
Are ty-wraps listed for use as NM cable supports or straps? Are they required to be?
Again, the code does not require that NM supports be listed, only approved.
Chris
A wire tie with a screw hole should work fine and should pass. There are a plethora of straps that are UL listed that should work fine, you just have to explore your options.
![]()
* High-Performance Cable Ties
* Ty-Rap(R)
* 316 stainless steel locking device in 6/6 nylon head maintains the right tension.
* Smooth, low-profile, no-notch body design is less stress-sensitive than notched ties, and infinitely adjustable. No-slip tail allows easier grasping for secure tensioning. Ribbed and stippled inner body keeps ties from slipping on the bundle. Black, weather-resistant, outdoor ties withstand temperatures ranging from -40 Degree to 185 DegreeF, except Thomas & Betts TY25MX-A and Thomas & Betts TY27MX-A, which withstand -40 Degree to 221 DegreeF.
* Natural-color ties are plenum rated
* Corrosion-resistant
* UL Registered under Standard 1565
* Qualified under OPC 23190
This is a circular argument. An AHJ approval, in many cases, will rely solely on a Listed product as evidence of meeting a standard that defines the performance and design characteristics of the product's intended use. This is why many fittings (especially cable) are specifically designed to be used with specific configurations/sizes of cable. The label on the packaging is required to indicate the listed use of the product (i.e. "use with 10/2 to 14/3 NM cable only"). In that case, does it mean you can also use it with MC/AC cable just because it seems to work OK?
IMHO...If an inspector requires a listed staple or strap, so be it. It's their decision which does not necessarily need an actual code article to support.
IMHO...If an inspector requires a listed staple or strap, so be it. It's their decision which does not necessarily need an actual code article to support.
Well...here is yet another example of using anything for any purpose - as long as it 'works'. What is the purpose of listing products, if this is acceptable? Why not use a piece of old nylon strapping across the romex and secure it with two drywall screws? Or better yet, use a protector plate bent over the romex and secure it with nails.
Well...here is yet another example of using anything for any purpose - as long as it 'works'. What is the purpose of listing products, if this is acceptable? Why not use a piece of old nylon strapping across the romex and secure it with two drywall screws? Or better yet, use a protector plate bent over the romex and secure it with nails.
I have an inspector really giving me a hard time about strapping romex. The issue is that I used 1 hole straps, anywhere from an MC strap to 1/2" emt strap to secure some romex running down a narrow channel, no other means is available (staples, CJs, stakits, etc.), doesn't work. Personally I've used one hole straps to secure romex for as long as I can remember and never had a problem, I cited 334.80 where it states specifcally straps in the paragraph and he still rejects it without any fact based code or literature. His solution is to rip down a wall (this is a remodel) just so I can get a different type of strap. I strongly believe I'm right, anyone know why straps would be unacceptable?
Also anyone know a code that says undercabinet lighting can not be daisy chained and must be run back to a junction point? Typically I do it that way but the sink is in an island and he also has a problem with this.
Size of the wiring compartment, perhaps? :-?
And now tell us it was "designed to be used that way "Why not use any of those things. :-?
I use romex sheath and two staples sometimes to secure multiple cables.
Exactly ........ why not?
If it secures the NM and does not damage the cable why not?
There is surely a reason the NEC does not require a listing for NM supports.
I use romex sheath and two staples sometimes to secure multiple cables.
And now tell us it was "designed to be used that way "