While I wasn't thinking of the ground being paralleled with the neutral as to be causing the current in the ground, simply because there is no load on the neutral to produce any current, but what about if at the transformer the neutral is connected to the XO, and the grounding conductor is connected to the transformer frame, which would also be connected to primary XO? and on to the MGN?
What if they are? They are still connected together although not directly, to create a parallel path. Now have a transformer with feed through primary conductors that go on to some other load(s) that uses the neutral, and throw in a poor connection someplace between where the two conductors in question are connected and now you have an alternate path of less impedance current is going to flow there, some will flow there if all connections are good but will be very small amount.
An inductive loop from not having all phase and neutral conductors in same raceway is also a possibility.
We need to ask OP if this objectionable current is still there if the main is open at the facility, that would indicate that it likely is coming from someplace outside the facility.