Ground and neutral are connected at the main panel coming from the meter base. For the townhouse I am working on the ground and neutral are connected in the electrical room for the bank of townhomes being served. All panels downstream must have the bonding screw removed from the neutral bar to the panel frame. Didn't find anything today, will be working on Saturday to hopefully find this. Plan to disconnect everything in the panel and test each incoming wire individually to try and pinpoint what circuit and hopefully find which area of the house is the cause
That's unnecessary waste of time. Disconnect electronics from coax so it no longer provides secondary ground path. Set up the two sockets with light bulbs I mentioned earlier. It doesn't take much load to notice an effect for a very loose or lost neutral. It'd take a high inrush such as a vacuum cleaner to produce noticeable brightening if it's only slightly loose. Provided that connection is good at the panel lug, the problem is outside of the homeowner's. You'll need to make impeccable documentation since there will be a question over who pays for appliance damage as well as replacing the section of damaged coax.
Check voltage between the neutral bar in the panel and a small part of feeder neutral with a line-to-neutral load in place. Aluminum wire issues can look fine to the eye when it is not fine electrically.
Ground does not carry current under normal conditions. Main breaker off. You should see 0v between incoming neutral and ground at breaker panel.
Check ohms between incoming neutral and ground. It should have a resistance indistinguishable from leads shorted together. No response on meter means open. Some resistance (higher than leads shorted together to couple thousands of ohms) means loose connection which means you have to call the power company which you people call the hydro.
Last edited: