I found the problem, but since this is the "Troubleshooting" forum I will let a few more people chime in as to what they think. I will give some more info though.
The stray voltage was real. I read 120V from a metal water spigot to anything around it that was metal, including building steel, garage door track, etc. I used the loZ function on my meter to eliminate ghost voltage. I even took my pigtail socket with a light bulb and it lit the bulb to full brightness to further substantiate the readings.
The voltage would go away with the main turned off. Now full disclosure, I didn't actually personally turn each breaker off but the tenant was doing that and the voltage remained. It only went away with the main off. Also, this may be suspect in that every circuit was turned off since the voltage would stop with the main off. The main was an old fused disconnect that fed a MLO panel and a couple of other fused disconnects.
The stray voltage was real. I read 120V from a metal water spigot to anything around it that was metal, including building steel, garage door track, etc. I used the loZ function on my meter to eliminate ghost voltage. I even took my pigtail socket with a light bulb and it lit the bulb to full brightness to further substantiate the readings.
The voltage would go away with the main turned off. Now full disclosure, I didn't actually personally turn each breaker off but the tenant was doing that and the voltage remained. It only went away with the main off. Also, this may be suspect in that every circuit was turned off since the voltage would stop with the main off. The main was an old fused disconnect that fed a MLO panel and a couple of other fused disconnects.