In many cases the source if the "stray" voltage is the primary neutral votlage drop, and that will not show up in this test.090706-2152 EST
electricalperson:
In your post #14 you ask about measuring the neutral drop from the transformer center tap to the main panel neutral bus. Measuring from the ground rod at the transformer to the main panel neutral bus will give you this information. This voltage drop includes the neutral wire from the transformer and any parallel paths. If you measure the current on said neutral wire, then you can calculate the resistance of said neutral wire. Then from knowledge of the wire length, material, and size calculate the resistance and see if there is reasonable correlation.
...
wheres the fun in that :grin:
It's done and I am on to the next thing. :grin:
090707-2227 EST
electricalperson:
If there is no neutral wire, it is totally burned out, no grounding to a copper water pipe system, the main panel connects to an 8 ft vertical ground rod, and a similar rod is at the transformer, then only loading one phase with for example 1 ohm and assuming the path resistance from one ground rod to the other is 50 ohms the voltage of the main panel relative to the transformer center tap is about 50*120/51 = 118 V.
.
50 ohms for the 2 ground rods, and 1 ohm for the load on the 1 phase
In many cases the source if the "stray" voltage is the primary neutral votlage drop, and that will not show up in this test.
There is much confusion and misapplication of the phrase "stray voltage/stray current".
As Don mentioned, and I want to emphasize, stray voltage is from the grounded/neutral conductor.
What some confuse this with is ground fault conditions.
It is generally easier to locate ground fault issues than it is to locate stray voltage issue.
Tell Me to watch Mike's video. http://www.mikeholt.com/strayVoltageVideo.php
I don't ever remember reading anything that has made this point. Could be I just can't add. Not saying you aren't correct and it may help in discussions here, but not much when talking to customers.
Customer: "I have stray voltage"
Me: "No, you have ground faults, not stray voltage."
Customer: "But I am getting shocked when I milk the cows!"
Me: "Voltage schmoltage!! It's a ground fault!"