J jslatter Member Oct 27, 2005 #1 When a 240v, 20 amp, street lighting branch circuit requires #8 AWG because of voltage drop, does the ground conductor also have to be #8?
When a 240v, 20 amp, street lighting branch circuit requires #8 AWG because of voltage drop, does the ground conductor also have to be #8?
iwire Moderator Staff member Location Massachusetts Oct 27, 2005 #2 Re: Street lighting ground conductor Yes. 250.122(B)