Hoping for a great weekend to all;
Termination Kits Manufactures offer what's know in the industry as " Rejackets ". this is nothing else but insulation hose ( Polymer ) that its installed over the length of the conductor after is has been strip out, the Stress Cone bottom end goes over the top end of the rejacket, bottom end of rejacket goes as far back to on the conductor as you may required. We have done a lot of it specially applycated to Multiconductors HV Cables, the
" Rejacketing " is installed as back as where the cable jacket was stripped out and a cable breakout boot is installed over to make the installation weather proof. 3M, Raychem, Prysmian Guard they all make this for different applications and voltage levels.
This statement does not answers the OP's question but will prevent having problems downsteams from where the conductors terminates as
RJ Wilson mentioned on his reply.
Regards.