This may not be the forum for this topic, but some of you may have run into a similar situation. Most people know that during a fire alarm the access controlled egress doors must unlock. This is a requrement of 2006 International Building Code (IBC) Chapter 10, section 1008.1.3.4.
The code requres that "...(exit doors) be installed in accordance with all of the following criterea:"
(I will paraphrase a bit for brevity)
1. A sensor that will unlock the door automatically when an occupant approaches the door.
2. Loss of power unlocks the door automatically.
3. A "PUSH TO EXIT" button provides a 'direct interruption of power to the lock'...
4. Fire Alarm causes door to unlock.
5. Sprinkler System causes door to unlock.
6. Occupancy groups A, B, E and M leaves door unlocked during business hours.
Now the question:
What about electric strike locks that require power to unlock (Fail-Secure)? They typically have a door handle or knob that can always be turned manually like any other door in order to exit the building.
The code doesn't seem to address the case of Fail-Secure devices. The language of this code would seem to require the use of Fail-Safe strike locks which have a constant power applied when locked and a loss of power will unlock the door.
In my experience Fail-Safe strike locks are expensive and wear out faster than Fail-Secure strike locks and this code seems to burden the customer unecessarily.
Has anyone else approached this problem and how did you resolve it with the local authority and the customer?
Thanks in advance for any help.
The code requres that "...(exit doors) be installed in accordance with all of the following criterea:"
(I will paraphrase a bit for brevity)
1. A sensor that will unlock the door automatically when an occupant approaches the door.
2. Loss of power unlocks the door automatically.
3. A "PUSH TO EXIT" button provides a 'direct interruption of power to the lock'...
4. Fire Alarm causes door to unlock.
5. Sprinkler System causes door to unlock.
6. Occupancy groups A, B, E and M leaves door unlocked during business hours.
Now the question:
What about electric strike locks that require power to unlock (Fail-Secure)? They typically have a door handle or knob that can always be turned manually like any other door in order to exit the building.
The code doesn't seem to address the case of Fail-Secure devices. The language of this code would seem to require the use of Fail-Safe strike locks which have a constant power applied when locked and a loss of power will unlock the door.
In my experience Fail-Safe strike locks are expensive and wear out faster than Fail-Secure strike locks and this code seems to burden the customer unecessarily.
Has anyone else approached this problem and how did you resolve it with the local authority and the customer?