1/2 of house goes dark,
Old dual bus GE panel, 2 ea 50 A 240 breakers feed A and B single phase breakers.
Old linen wire in conduit.
a. electric razor uses same outlet in bathroom for many years
b. 6-23 screws holding receptacle become loose after a few decades
c. top retaining screw head works thru outlet top slot, now a 1/8" movement possible every time electric shaver used.
d. more years - linen wears thru where bearing against box, short
e. BOTH 20A branch and 50A sub main breakers trip.
f. happily, enough slack in box to trim linen wire and reterminate, replace outlet, etc, all is well.