Strobe requirements

Status
Not open for further replies.

Gategator37

Senior Member
Besides adding strobes for areas that have an ambient of over 105db, where else are they required? Anywhere that a deaf person could regularly be?
 

dhalleron

Senior Member
Location
Louisville, KY
This post might fit better in the Low Voltage and Limited Energy section.

Basically everywhere that is a public or common use area such as bathrooms, conference rooms, break rooms, hallways, and common areas. An area with cubicles would need them, but an office for just one person might not unless it is designated for a hearing impaired person. Some AHJ's consider an office with a meeting table or second chair as a conference room and will require a strobe.
 

nhfire77

Senior Member
Location
NH
Strobes (if you are referring to fire alarms) are pretty much required everywhere:

ADA rules, see the ADAAG.

Also read 2010 NFPA 18.5 and 18.6 Visible Characteristics of Notification Appliances
 